    Mr. Cool Mini Split DIY: Not heating properly

    Installed Mr. Cool Mini split last year. It is a DIY. Easy to install and had electrican do the wiring. Heat was great last year and AC this summer was fantastic. This season, having issues all over. Not going above 60 degrees. Enters defrost mode constantly, and has a slight drip on one side. Anyone have any experience with these and some of the issues? I hear HVAC guys won't work on them since they are DIY, but was not aware of that issue at time of purchase.

  2. Member
    Join Date
    Jun 2012
    Location
    tennessee
    Posts
    6,578
    #2
    May be low on Freon, due to leak

  3. Member
    Join Date
    Feb 2018
    Location
    Isanti, Minnesota
    Posts
    1,025
    #3
    I can understand why a lot of hvac guys won't work on a dyi install. First thing i would do is pull the refrigerant out and pressure test with nitrogen. 90% of issues with mini splits are install or leak related.

  4. Member
    Join Date
    Jul 2007
    Location
    Redding Ca
    Posts
    1,007
    #4
    Is there a problem the temperature sensor?

  5. Member
    Join Date
    Dec 2007
    Location
    Pompton Lakes
    Posts
    2,771
    #5
    No idea. I know nothing about HVAC.
    Quote Originally Posted by kacordy View Post
    Is there a problem the temperature sensor?

  6. Member
    Join Date
    Sep 2016
    Location
    Louisville Ky
    Posts
    15,827
    #6
    WEll it is called Mr Cool not Mr Heat!!!!! Kidding I couldnt help myself.

  7. Member
    Join Date
    Jan 2014
    Location
    Pickwick lake, Iuka Ms.
    Posts
    16,324
    #7
    You are low on refrigerant most likely

  8. Member Rick H's Avatar
    Join Date
    Sep 2011
    Location
    Northern Cincinnati Ohio Close Enough like it or not its where I am
    Posts
    3,794
    #8
    Should still be under warranty. Give them a call.

    Steve McQueen "Le Mans"
    Own the Champ! Life Long Petty Fan!

    2003 ChampioN 2006 250 Merc. XB, Prop By Mark C.
    2002 Ranger Okeechobee Special EvinRude Ficht 90 / 9.9 4-Stroke GLAD to have a Get me to the Dock motor maybe!

  9. Member
    Join Date
    Jan 2015
    Location
    Spartanburg sc
    Posts
    1,059
    #9
    In my experience, across most mfg's- leaking refrigerant (flares most of the time), dirty evap/filter, or clogged drains are 90% of our service calls with minisplits.

    Was this a precharged system or one that required evacuation?
    Skeeter Sx186 w/ yamaha 150

  10. Member
    Join Date
    May 2012
    Location
    Greenwood, SC
    Posts
    646
    #10
    Post #3 sums it up. It’s probably low on refrigerant due to a leak at the connections. Most flares are not done with proper tools and the connection should have nylog or some sort of connection approved material on the male side.

  11. Member
    Join Date
    Mar 2023
    Location
    Franklin TN
    Posts
    499
    #11
    Quote Originally Posted by Perchpro View Post
    I can understand why a lot of hvac guys won't work on a dyi install. First thing i would do is pull the refrigerant out and pressure test with nitrogen. 90% of issues with mini splits are install or leak related.
    This 100%

  12. Member
    Join Date
    Apr 2021
    Location
    Towson, Md
    Posts
    2,138
    #12
    Quote Originally Posted by Chadsc View Post
    In my experience, across most mfg's- leaking refrigerant (flares most of the time), dirty evap/filter, or clogged drains are 90% of our service calls with minisplits.

    Was this a precharged system or one that required evacuation?
    I have installed several Mr. Cool mini splits with no issues. (so far).
    I believe all of these units come pre charged and the only tools required for the flare connections are two open end wrenches.

  13. Member
    Join Date
    Dec 2007
    Location
    Pompton Lakes
    Posts
    2,771
    #13
    I have a guy coming to look at it on Saturday. A couple other guys said they wouldn't look at Mr. Cool.

  14. Member
    Join Date
    Jan 2014
    Location
    Pickwick lake, Iuka Ms.
    Posts
    16,324
    #14
    I have installed two and both are flawless. Any brand can put out a bad one every now and then. So I still stick with the leak theory or some how some part when vacuumed did not seal. If it ever worked correctly it simply has a leak.

  15. Member
    Join Date
    Oct 2007
    Location
    Haughton, La
    Posts
    5,358
    #15
    Most issues relate to refrigerant issues. Critical on installing for and low micron evacuation and pressurized the line and evaporator. Occasionally you can have sensor and board issues. The flare nuts on refrigerant line connections on a new system are highly probable for a leak. It doesnt take much of a refrigerant leak, just a few ounces kills performance. They are supposed to torqued to certain specs per size. The have wrenches made specifically for that purpose.
    2014 Phoenix 721XP, 250 SHO, Bobs Action Jack, Dual Blades, 112 Ultrex, Garmin Echomap Ultra's Networked, NMEA 2000, 2019 Lariat FX4 F150 Supercrew 4x4
    2001 Bumblebee 2100 Super Vee Mercury 225 EFI
    1988 Hydrasport Kevlar hull 115 Tower of Power

  16. Member
    Join Date
    Jan 2015
    Location
    Spartanburg sc
    Posts
    1,059
    #16
    Quote Originally Posted by Aj14 View Post
    I have installed several Mr. Cool mini splits with no issues. (so far).
    I believe all of these units come pre charged and the only tools required for the flare connections are two open end wrenches.
    If this is the case, I would be very surprised if most homeowners are using torque wrenches on those flares. And then if a flare is to be made, how many are using a 37-vs-45* orbital flare cone.
    Skeeter Sx186 w/ yamaha 150

  17. Member Rick H's Avatar
    Join Date
    Sep 2011
    Location
    Northern Cincinnati Ohio Close Enough like it or not its where I am
    Posts
    3,794
    #17
    Updates?

    Steve McQueen "Le Mans"
    Own the Champ! Life Long Petty Fan!

    2003 ChampioN 2006 250 Merc. XB, Prop By Mark C.
    2002 Ranger Okeechobee Special EvinRude Ficht 90 / 9.9 4-Stroke GLAD to have a Get me to the Dock motor maybe!

  18. Member
    Join Date
    Apr 2016
    Location
    Mountain Home, AR
    Posts
    10,284
    #18
    That was LAST JANUARY !!!

  19. Member
    Join Date
    Jan 2014
    Location
    Pickwick lake, Iuka Ms.
    Posts
    16,324
    #19
    Got two units. Flares are factory made. One is 3 years old and working great. The other is only 6 months old and currently keeping me warm as I type. If it just not getting warm enough it’s a good chance it is low on refrigerant. But can be other things. Testing connections is a must when installing.