    Wire gauge question

    I have an older MK Terrova….12v… 55lb thrust…has 50amp circuit breaker in the line…in you folks professional opinion would 8ga wire be optimal from battery to the circuit breaker or should I go to 6ga? Using marine grade tinned wire and Ancor ring terminals…thank you in advance

  2. Member st041986's Avatar
    Join Date
    Jul 2010
    Location
    Bland, Missouri
    Posts
    1,690
    #2
    If it's a short run, you could go with either. I'd go with 6ga if it fits. The less voltage drop, the better.
    *******************************
    2017 Legend SS 1860 Semi-V
    2013 Evinrude Etec 150/105 jet drive
    Minn kota Ultrex Quest Trolling Motor
    Humminbird Helix 9 Chirp Mega SI GPS G2N (console)
    Garmin Echomap Ultra 106sv with LVS32 transducer (bow)
    *******************************
    YouTube: youtube.com/Etec86

  3. Member
    Join Date
    Jan 2017
    Location
    Tennessee
    Posts
    189
    #3
    thatd be fine for a 45 lb but not a 55lb. needs a 60a breaker and the wire awg would depend on length. 8awg is only good for 5ft and 10ft requires 4awg. from 11 to 20ft requires 2awg.

  4. Member
    Join Date
    Jan 2019
    Location
    North Carolina
    Posts
    10
    #4
    Thank you folks for your responses

  5. Member
    Join Date
    May 2011
    Location
    Chesapeake, VA
    Posts
    1,737
    #5
    https://minnkota-help.johnsonoutdoors.com/hc/en-us/articles/9014173682455-Conductor-Gauge-and-Circuit-Breaker-Sizing-Chart
    Lightning 6
    2007 TR-196DC

  6. Member
    Join Date
    Oct 2013
    Location
    Cartersville, Ga.
    Posts
    139
    #6
    There is a new chart but the old one said 4 awg. I had a 55 once and used the 4 awg. I'm not sure why mk changed the chart....voltage drop math hasn't changed.

  7. Member
    Join Date
    Jan 2017
    Location
    Tennessee
    Posts
    189
    #7
    Quote Originally Posted by JK9027 View Post
    There is a new chart but the old one said 4 awg. I had a 55 once and used the 4 awg. I'm not sure why mk changed the chart....voltage drop math hasn't changed.
    the old chart calculates out to a 10% voltage drop. 3% and 105 deg conductor really should be used because if the big motor fails the TM beckmes a critical piece of equipment.

  8. Member
    Join Date
    Feb 2016
    Location
    Toronto, ON, Canada
    Posts
    345
    #8
    1995 Champion 190 dcx Elite

  9. Member justinp61's Avatar
    Join Date
    Sep 2010
    Location
    Smithland KY
    Posts
    862
    #9
    My boat came with 8 gauge wire and a Maxxum 80lb thrust trolling motor, I replaced it with a Fortrex, both draw about 56 amps full load. In 13 years, the only issue I ever had was a TM plug that was only rated for 40 amps. I pulled the 8 gauge and replaced it with 6 gauge when I upgraded to a Ghost. The old 8 gauge replaced the 10 gauge that was feeding my fuse panel at the console.