    wheres the electricians at? voltage drop

    Looking for an aluminum overhead drop wire to fit the below. What gauge wire is needed.
    200 amp breaker box at entrance, then 800' run to camp. Camp is a double wide trailer with central A/C

  2. Member
    Join Date
    Apr 2012
    Location
    Loganville GA
    Posts
    1,021
    #2
    At that distance you would have to go with at least 700 KCMIL in aluminum to sustain 150 amps at 240V to have less than 3% drop.

  3. Electrical/Wiring/Trolling Motors Moderator CatFan's Avatar
    Join Date
    Jun 2004
    Location
    SW Indiana
    Posts
    26,088
    #3
    This is the reason they run power at high voltage and step it down very close to the point of use. Compare your cost to having a HV service line run with the cost of such cable and the poles and hardware that would be required to support it. Not going to be cheap.
    If you have integrity, nothing else matters. If you don't have integrity,
    nothing else matters.​

  4. BBC SPONSOR
    Join Date
    Jun 2008
    Location
    Tampa
    Posts
    527
    Bob's Machine - Action Series Jack Plates - DeckPlugs - DeckSavers - QuickSlip - The Big D Trolling motor handle - Much more!
    www.bobsmachine.com

  5. Member
    Join Date
    Dec 2010
    Location
    Franklin,OH
    Posts
    647
    #5
    You need to base the voltage drop on how many amps you will actually be pulling with a small buffer added, there are free sites online with voltage drop calculators.

  6. Banned
    Join Date
    Dec 2010
    Location
    Olympia Washington
    Posts
    10,856
    #6
    .
    Last edited by Clif Kincaid; 04-18-2019 at 04:47 PM.

  7. Hunting & Gun Lodge Moderator Roddy's Avatar
    Join Date
    Jun 2004
    Location
    Murray / KY lake
    Posts
    16,843
    #7
    My advice, Get a pole and meter set.
    SIMMONS CUSTOM BOATS
    Anderson Services LLC
    " Those who beat their swords into plowshares will plow for those who don't"

    Bring Back Gluten!!!

  8. Member
    Join Date
    Jan 2007
    Location
    Allentown,Pa.
    Posts
    2,257
    #8
    Aside from the cost and how hard 800mcm would be to work with you won't find a meter can or 200a panel with breaker lugs big enough to fit that let alone getting into the panel.

  9. Moderator JerryT's Avatar
    Join Date
    May 2004
    Location
    90210
    Posts
    21,222
    #9
    Quote Originally Posted by Clif Kincaid View Post
    .
    Nailed it ...... lol

  10. Member
    Join Date
    Jun 2004
    Location
    Kennebunkport, Maine
    Posts
    1,357
    #10
    Trench along the driveway bury a 4" and two 3" conduits. Pull in the primary in the 4" to a transformer pad. Put transformer within 100' of camp. Then run from there to the camp with the secondary. Should be able to do all that for around 10-12 grand. No biggie right. We here at BBC all pay cash for everything. The 3" would be for cable and telephone.

  11. Member Champ891's Avatar
    Join Date
    Nov 2013
    Location
    Bethal Springs, Tn
    Posts
    8,236
    #11
    Quote Originally Posted by Roddy View Post
    My advice, Get a pole and meter set.
    This

  12. Member
    Join Date
    Dec 2015
    Location
    Alabama
    Posts
    21,605
    #12
    That is along run at load voltage.