    Question Breaker Size 36 VDC

    Installed Fortrex 36 VDC 112 thrust with 6 gauge wire. What size amp breaker is recommended?

    thanks

    21 XD 225 Merc

  2. Electrical/Wiring/Trolling Motors Moderator CatFan's Avatar
    Join Date
    Jun 2004
    Location
    SW Indiana
    Posts
    26,089
    If you have integrity, nothing else matters. If you don't have integrity,
    nothing else matters.​

  3. Member
    Join Date
    Nov 2009
    Location
    Lexington S.C.
    Posts
    7,821
    #3
    Thanks for link!! I posted something earlier about wire size and was advised to run 6 gauge. Minn Kota advice is 8 gauge. Thoughts

    21 XD 225 Merc

  4. Member
    Join Date
    Jan 2005
    Location
    Texarkana
    Posts
    18,963
    #4
    Quote Originally Posted by SC Bullet View Post
    Thanks for link!! I posted something earlier about wire size and was advised to run 6 gauge. Minn Kota advice is 8 gauge. Thoughts
    The conductor gauge chart that MinnKota is using goes up to 25' and does show 8ga for the 112. However, if the boat is big enough for a 112, it is probably somewhere between a 19' and 22' boat. Lets use a 20' boat for example. With a 20' boat you will have somewhere around 45' of wire, or an additional 20' that MinnKota's chart does not take into consideration. Remember, on DC wiring you have to go from negative back to positive -- and across all the jumpers. While it's true that anywhere the amps are measured on that wire, it is going to be apx 52A (suggested amp draw for the 112), the length of the wire will dictate the diameter of the wire (gauge) that needs to be used to help eliminate resistance and voltage drop. This is the reason to use 6ga on that long of run.
    BBC Sponsor since 2006: (870) 773-3474
    Mon - Thrs 8am - 5pm Central
    Friday 8am-12pm
    Garmin Certified Dealer and Installers: Call us for all your Garmin Electronics needs!
    ASC for: Garmin, Lowrance, Minnkota, Humminbird, and Powerpole.
    [SIGPIC] http://www.jonestrollingmotor.com
    [/SIGPIC]

  5. Electrical/Wiring/Trolling Motors Moderator CatFan's Avatar
    Join Date
    Jun 2004
    Location
    SW Indiana
    Posts
    26,089
    #5
    6 is better.
    If you have integrity, nothing else matters. If you don't have integrity,
    nothing else matters.​

  6. Member
    Join Date
    Nov 2009
    Location
    Lexington S.C.
    Posts
    7,821
    #6
    Quote Originally Posted by Jonestrollingmotor View Post
    The conductor gauge chart that MinnKota is using goes up to 25' and does show 8ga for the 112. However, if the boat is big enough for a 112, it is probably somewhere between a 19' and 22' boat. Lets use a 20' boat for example. With a 20' boat you will have somewhere around 45' of wire, or an additional 20' that MinnKota's chart does not take into consideration. Remember, on DC wiring you have to go from negative back to positive -- and across all the jumpers. While it's true that anywhere the amps are measured on that wire, it is going to be apx 52A (suggested amp draw for the 112), the length of the wire will dictate the diameter of the wire (gauge) that needs to be used to help eliminate resistance and voltage drop. This is the reason to use 6ga on that long of run.
    Thanks for explaining John..

    21 XD 225 Merc

  7. Member
    Join Date
    Apr 2009
    Location
    The lands of the former Republic of Texas
    Posts
    3,497
    #7
    Quote Originally Posted by SC Bullet
    I posted something earlier about wire size and was advised to run 6 gauge. Minn Kota advice is 8 gauge. Thoughts
    SC,

    Minn Kota's table does correctly consider total wire lengths..... It is being expressed as stated here:

    *Wire Extension Length refers to the distance from the batteries to the trolling motor leads.
    So 8AWG according to MinnKota (and as well well published wire tables*) would have been adequate for your install < 25' run (~50 feet for total circuit) and have fully met the no more than 5% voltage loss at max amp draw needs of your trolling motor.


    (50 feet of 8AWG results in a voltage loss of no more than 5% of the trolling motor batteries total voltage output.)



    Last edited by Lou r Pitcher; 10-17-2018 at 10:04 AM.