    Blue Sea Fuse Block correct wire gauge

    Will be installing a Blue Sea fuse block 12 circuit w/ground bus this weekend.

    1. What is the correct wire gauge size from the battery to the fuse block? (there will be a 30 amp breaker in this run.)

    2. What is the correct wire gauge size from the fuse block to the various accessories. (4 Lowrance HDS units for starters)

    Thanks in advance.

  2. Member
    Join Date
    Mar 2006
    Location
    Beaufort
    Posts
    1,110
    #2
    It depends on the distance the fuse block is from the battery.
    3 feet 10 gauge
    10 feet 8 gauge
    20 feet 6 gauge

  3. Member ifishinxs's Avatar
    Join Date
    Jul 2015
    Location
    Southern Utah
    Posts
    6,452
    #3
    10 gauge is ideal but It really depends on your current draw from the fuse panel. It your just running a few graphs 12 gauge will be fine. Larger gauge will give you less current drop.
    2024 Phoenix 818, Mercury 175 (3B414035) Trick Steps, 3 Garmin 106 SV,s, LVS 34. BoatEFX dual bow mount. Ionic 12V 125AH, 2 12V 100 ah LiTime’s for the TM. Minn Kota 345 PCL charger,

  4. Member
    Join Date
    Jan 2005
    Location
    Texarkana
    Posts
    18,962
    #4
    Quote Originally Posted by ifishinxs View Post
    10 gauge is ideal but It really depends on your current draw from the fuse panel. It your just running a few graphs 12 gauge will be fine. Larger gauge will give you less current drop.
    If he's going to use a 30A breaker, 12 gauge is not "fine". Depending on how far from the battery will depend on carrying capacity for the 10ga. He stated a 12 circuit fuse block and initially his graphs. The OP needs to plan for what else may be fused off this block. I would suggest 8ga so he can go with a 40A breaker later down the road if needed.
    John
    BBC Sponsor since 2006: (870) 773-3474
    Mon - Thrs 8am - 5pm Central
    Friday 8am-12pm
    Garmin Certified Dealer and Installers: Call us for all your Garmin Electronics needs!
    ASC for: Garmin, Lowrance, Minnkota, Humminbird, and Powerpole.
    [SIGPIC] http://www.jonestrollingmotor.com
    [/SIGPIC]

  5. Member
    Join Date
    Jul 2017
    Location
    Lower, Alabamer
    Posts
    450
    #5
    Getting ready to do the exact same thing on my boat with the same Blue Sea fuse block. Here's an excerpt from the ABYC Handbook:

    How to Choose Marine Wire Size:


    There are three factors when choosing the right wire gauge:

    1. Current draw of the device – measured in Amps
    2. Total length of the run – measured in feet as a “round trip”
    3. Allowable voltage drop – measured in % loss of voltage

    ABYC says that non-critical loads like a livewell, or courtesy lights should have no more than a 10% voltage drop, while critical loads like a bilge pump or navigation lights should have no more than a 3% voltage drop.
    Remember, length of the run is a “round trip”… so from the battery, out to the load and back. Example calculations are below the table.
    Example 1:
    Your livewell pulls 6A. There is 10 feet from the battery to the switch panel, then 5 more feet from the switch panel to the console livewell.
    Length of run is 10 + 5 + 5 + 10 = 30ft (from battery to load, and back again)
    On a livewell a 10% voltage drop is acceptable, so we use the top table. We’ll round up the 6A, to 10A, and use 14AWG wire.
    Example 2:
    Your LED navigation lights pull 3A. There is 10ft from the battery to the switch panel, then 14ft of wire from the switch panel to the lights.
    Length of run is 10 + 14 + 14 + 10 = 48ft (from the battery to load, and back again)
    Navigation lights are critical, so only 3% voltage drop is allowed, so we use the bottom table. We’ll round the 3A up to 5A, and 48ft up to 50ft, and use 10 AWG wire.


  6. Member
    Join Date
    Apr 2009
    Location
    The lands of the former Republic of Texas
    Posts
    3,497
    #6

    I agree and use the wire selection method presented above by bgtoot and ABYC that is considering the 'Allowable Voltage Drop. I prefer to use for the value of 'Total Current', the actual manufacturer's (Blue Sea Systems) carrying capacity of the fuse panel even if at time of the installation the panel'capacity is not going to be used fully. As the panel may be used to power electronics, the max total voltage dropped is 3% (not 10%) for the full circuit path. (I prefer for the fuse panel's battery side of the circuit to have only a 1 to 1 & 1/2% max drop.

    For me, the suggested use of 'carrying capacity' of a given wire size is never a good method to use for selecting boat wiring as doing so permits far too high of a voltage drop. Excessive voltage drops can cause sensitive electronics to reset or shut down such as when an engine is cranked or a tilt motor's stall limit is reached.