    Breaker switch for 36V/112lb Ultrex

    The breaker, on/off switch I have now is:

    FL. AMP= 50
    TRIP AMPS= 67.5

    Is this ok for a 36V Ultrex?

    Thanks! Scott
    Scott Inman

  2. Electrical/Wiring/Trolling Motors Moderator CatFan's Avatar
    Join Date
    Jun 2004
    Location
    SW Indiana
    Posts
    26,088
    If you have integrity, nothing else matters. If you don't have integrity,
    nothing else matters.​

  3. Member fishnfireman's Avatar
    Join Date
    Apr 2005
    Location
    Amarillo
    Posts
    12,496
    #3
    It will work until the first time you need to run at a higher setting for any length of time. I have a friend who has been running his original 50
    for almost a year now. Every time I see him he just shakes his head and says (No not yet)……….. Best to replace first chance you get.

  4. Member
    Join Date
    May 2005
    Location
    Fogelsville, PA
    Posts
    479
    #4
    Quote Originally Posted by fishnfireman View Post
    It will work until the first time you need to run at a higher setting for any length of time.
    That's a fact....popped my 50amp breakers (on 36 volt Ultrex) just past weekend on an electric only lake from running at high for 10 minutes....that wire around the 50amp breaker
    on my jumper wire got hot-hot-hot!!
    Replaced with the 60amp Minn Kota breaker...was a good time to replace some of the old original factory installed cable lugs that
    had some corrosion.....used heat shrink and a hydraulic crimper for my new lugs.....

  5. Member
    Join Date
    Jul 2017
    Location
    Lower, Alabamer
    Posts
    450
    #5
    Quote Originally Posted by SeanH View Post
    That's a fact....popped my 50amp breakers (on 36 volt Ultrex) just past weekend on an electric only lake from running at high for 10 minutes....that wire around the 50amp breaker
    on my jumper wire got hot-hot-hot!!
    Replaced with the 60amp Minn Kota breaker...was a good time to replace some of the old original factory installed cable lugs that
    had some corrosion.....used heat shrink and a hydraulic crimper for my new lugs.....
    I understand the situation and I don’t have an Ultrex installed, but if the wires were hot with the 50 amp breaker wouldn’t you WANT it to trip early? If replaced with a 60 amp and the wires get hot again, it would take longer to trip potentially causing a fire before tripping?

  6. Member
    Join Date
    Jan 2005
    Location
    Texarkana
    Posts
    18,962
    #6
    Yes, you want the breaker to trip before the wires get hot. I would guess the poster with the hot wires either wasn't using the correct wire size for the breaker or had some connections that caused the wire to heat. You do need the 60A breaker for both the 80 and the 112, even if MinnKota's website says 8ga and 50 is OK, use 6ga and 60A
    John
    BBC Sponsor since 2006: (870) 773-3474
    Mon - Thrs 8am - 5pm Central
    Friday 8am-12pm
    Garmin Certified Dealer and Installers: Call us for all your Garmin Electronics needs!
    ASC for: Garmin, Lowrance, Minnkota, Humminbird, and Powerpole.
    [SIGPIC] http://www.jonestrollingmotor.com
    [/SIGPIC]

  7. Member
    Join Date
    May 2005
    Location
    Fogelsville, PA
    Posts
    479
    #7
    John is correct....yes, I have 6 gauge wires....but....my 50amp manual reset breakers were a few years old, and likely had internal corrosion, causing resistance, and that area to heat up.....they are a maintenance/replacement item I've learned....

  8. Member
    Join Date
    Oct 2005
    Location
    Oaks, PA
    Posts
    1,159
    #8
    Quote Originally Posted by scotti509 View Post
    The breaker, on/off switch I have now is:

    FL. AMP= 50
    TRIP AMPS= 67.5

    Is this ok for a 36V Ultrex?

    Thanks! Scott
    Quote Originally Posted by CatFan View Post
    No, you need a 60A


    how can you say that? without asking wire size.

    Breaker size is strictly determined by wire size. Nothing else. It doesn't matter what motor you have. Size the wire based on the current draw of your motor.

  9. Electrical/Wiring/Trolling Motors Moderator CatFan's Avatar
    Join Date
    Jun 2004
    Location
    SW Indiana
    Posts
    26,088
    #9
    Quote Originally Posted by Team Dougherty View Post


    how can you say that? without asking wire size.

    Breaker size is strictly determined by wire size. Nothing else. It doesn't matter what motor you have. Size the wire based on the current draw of your motor.
    Read the link.
    If you have integrity, nothing else matters. If you don't have integrity,
    nothing else matters.​

  10. Go With God ! scotti509's Avatar
    Join Date
    Jan 2008
    Location
    Spokane, Wa.
    Posts
    378
    #10
    II ordered a Bussman 60 Amp
    Scott Inman

  11. Member
    Join Date
    Oct 2005
    Location
    Oaks, PA
    Posts
    1,159
    #11
    Quote Originally Posted by CatFan View Post
    Read the link.
    I did 50 amp on 10 awg. Is out of spec. Would not be wise to follow that.

  12. Member
    Join Date
    Jan 2005
    Location
    Texarkana
    Posts
    18,962
    #12
    Quote Originally Posted by Team Dougherty View Post
    I did 50 amp on 10 awg. Is out of spec. Would not be wise to follow that.
    That's for 5 or 10ft -- but true, I wouldn't follow that part of the chart, but MinnKota uses 10ga from trolling motor to the plug on all of the trolling motors.
    BBC Sponsor since 2006: (870) 773-3474
    Mon - Thrs 8am - 5pm Central
    Friday 8am-12pm
    Garmin Certified Dealer and Installers: Call us for all your Garmin Electronics needs!
    ASC for: Garmin, Lowrance, Minnkota, Humminbird, and Powerpole.
    [SIGPIC] http://www.jonestrollingmotor.com
    [/SIGPIC]

  13. Member
    Join Date
    Sep 2013
    Location
    Southern Kansas
    Posts
    487
    #13
    Quote Originally Posted by Jonestrollingmotor View Post
    That's for 5 or 10ft -- but true, I wouldn't follow that part of the chart, but MinnKota uses 10ga from trolling motor to the plug on all of the trolling motors.
    And that's why I cut the power lead wires as short as possible to reach my power source. I know it's ok, but that seems awful light gauge for a 50-60a motor.
    Last edited by rat0502; 09-13-2019 at 03:32 PM. Reason: Plural.......
    1998 Tr-21, 2001 Yamaha 225 OX66

  14. Member fishnfireman's Avatar
    Join Date
    Apr 2005
    Location
    Amarillo
    Posts
    12,496
    #14
    Quote Originally Posted by rat0502 View Post
    And that's why I cut the power lead wires as short as possible to reach my power source. I know it's ok, but that seems awful light gauge for a 50-60a motor.

    That 10ga power lead still makes me shake my head..