To begin with, lithium batteries, from my experience, have a resting voltage around 13.3v. This yields 39.9v for a 36v system when using three (3) lithium batteries in series. Depending on the load applied, the voltage will drop from 13.3v to 12.5v or so (I have seen as low as 12.4v on a 24v Ultrex with 6awg). My most recent measurements and experience are as follows:
- Three (3) 50aH Ionic batteries in series
- Ultrex Quest 36v trolling motor
- 2AWG Ancor Tinned Copper Marine Grade wire - approximately 25' run one way
Capture.PNG
At full rip (setting 10) the Ionic iPhone app shows 59a draw and 12.5v/battery. This can be confirmed with the formula for voltage drop, which is VD=2*L*R*I. To utilize this formula, we must know the impedance of the 2AWG Ancor wire, which according to Ancor's Primary Wire Battery Cable Chart is .16 ohms @ 1000'. Impedance @ 1' would be .00016 ohms.
VD: 2*25*.00016*59 = .472v
13.3v - .472v = 12.828v
While the calculation above doesn't align directly with real-world results, it is close enough for discussion purposes understanding that other variables are at play (terminations, fused connections, etc.).
With all that being said, a more effective way to address bishoptf's concern might be "Use a breaker that complies with the specified amperage rating from the manufacturer of the trolling motor". The Garmin Force specifies a 60a breaker, so there is your answer. Any less, and you run the risk of tripping the breaker.
Additionally, there is concern regarding the factory 6AWG trolling motor wire. You can modify the voltage drop formula to determine wire selection (or adequacy), which would be R=(VDx1000)/2*L*I. For this, we need to specify the desired maximum voltage drop, and we will use 3%. To input this into the formula we need actual voltage after drop = .03*39.9 = 1.197v.
(1.197*1000)/(2*25*59) = .4 ohms per 1000'
Ancor Marine Grade Primary Wire & Battery Cable @ 6awg is rated at .4 ohms/1000', therefore this should work. There again are other variables at play (battery type, terminations, fused connections, additional wire not accounted for, etc.) that will negatively impact this best-case scenario equation. I would advise erring on the side of caution and upgrading to 4AWG or even 2AWG (which is what I did), but that would apply more for a new install or if the decision had already been made to pull new wires.
As an aside, it is easy to get buried in the details when considering this, as this discussion is centered around the trolling motor being on its highest speed. This happens infrequently for most, but in the event of an emergency (big motor down), you want to rest assured that the trolling motor will serve you without fail.
In summation, use a 60a breaker and the existing 6AWG should be adequate. For new installs or re-rigging, I would advise using the same 60a breaker and consider 4AWG or even 2AWG marine grade tinned copper wire.